Mike,

I disagree that my observations rely on the portion of optics in the SONET/SDH market.  I am simply using the SONET/SDH application data to illustrate that short-reach SM optics comprise only a small fraction of the total SM optics for SONET/SDH.  I then apply this observation to Ethernet application space.  As a result, the 4% allocation I suggested as a default grant to Ethernet SM optics in data centers is likely generous for two reasons.  1) I suspect that the portion of short-reach SM optics would be higher for SONET/SDH than for Ethernet because SM optics are more preferred by carriers, the primary users of SONET/SDH, than by enterprise customers, and 2) the short-reach optics in this bin in the barbieri contribution include both 2km and 7km variants, only a fraction of which would actually be deployed in COs or DCs.  Some would be deployed between COs and in campuses.  If these two items were properly accounted for, the grant to SM Ethernet optics in DCs would drop below 4%. 

 

I also disagree that the ratio of 10G-LR to 10G-SR is a good grant to SM deployments in DCs at any data rate.  On one hand, while I have not tried to employ the data details from the barbieri reference to hone this analysis, a grant larger than 4% during the early phase of deployment might be more reasonable given that this data shows that historically SM optics are deployed earlier than MM.   On the other hand, a 20% grant as the application reaches maturity is the same as saying all SM deployments are in DCs and none are in spaces outside DCs, which is obviously way off.  Further, the cost disparity favoring MM optics at 100G is far higher than at 10G which would tend to skew even the early 100G deployments towards MM.  This disparity is very real and causing market acceptance barriers today. 

 

To conclude, I cannot see justification for LR4 grants.  However, a grant of a few percent might be reasonable for SM variants that close the cost disparity to something similar to that observed between 10G-LR and 10G-SR.  But if such a grant is applied to SM optics, then a grant should also be applied to MM optics over lower capability options like copper.  From where I stand today such fine tuning is not worth the effort given the elevated risk of analysis paralysis that accompanies it. 

 

Regards,

Paul

 


From: Mike Dudek [mailto:mike.dudek@xxxxxxxxxx]
Sent: Monday, November 28, 2011 3:39 PM
To: Kolesar, Paul; STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: RE: [802.3_100GNGOPTX] Emerging new reach space

 

It looks as though I mis-interpreted the numbers.    I would point out however that your argument is relying on the fact that the SONET/SDH is a significant proportion of the overall market.   If it is not then the percentage of these links that are less than 7km is irrelevant.   I believe the best number to use for this analysis would be the ratio between  useage of 10GBASE-LR modules and 10GBASE-SR modules.   I would be surprised if it is only 4%.

 

Mike Dudek 

QLogic Corporation

Senior Manager Signal Integrity

26650 Aliso Viejo Parkway

Aliso Viejo  CA 92656

949 389 6269 - office.

Mike.Dudek@xxxxxxxxxx

 

 

From: Kolesar, Paul [mailto:PKOLESAR@xxxxxxxxxxxxx]
Sent: Monday, November 28, 2011 12:24 PM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Mike,

You make good observations.  But please note that the ~80/20 split includes all usage not just within a data center.  The barbieri reference cited below also shows on slide 9 that for SONET/SDH the percentage of sub 7km SM optics deployed is less than 20% of the overall SM mix.  And this is for an application that sees much less MM deployment compared to Ethernet.  So while I think your argument has validity, the ratios may need adjustment.  Instead of assuming 20% SM ports in DCs, the SONET/SDH data suggests that it may be more accurate to assume less than 1/5th of this (< 4%) of the total SM ports are in DCs.  So rather than 20% + 0.8*(SM coverage), it may be better to use 4% + 0.96(SM coverage). 

 

Paul

 

 


From: Mike Dudek [mailto:mike.dudek@xxxxxxxxxx]
Sent: Monday, November 28, 2011 1:25 PM
To: Kolesar, Paul; STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: RE: [802.3_100GNGOPTX] Emerging new reach space

 

On the topics of volume I think we need to be clear that the 20% SMF to 80% MMF is not a fixed ratio.    I think that the ratio should be mainly explainable by the capabilities of the units.   At the moment the MMF is sufficiently lower cost than SMF that within the data center most installations use MMF when they can and SMF when MMF hasn’t got the reach.    If the MMF reach becomes shorter it’s volume will drop and the SMF volume will increase.   That is evident in Paul’s spreadsheet (and is I think one of the basic assumptions in his spreadsheet).    Looking at that spreadsheet however there is obviously some additional usage for SMF at 10G because if one puts 300m for the multimode solution it predicts that the SMF percentage is well less than 2%.     Based on this I think we could assume that the SMF percentage will be approximately 20% + .8*(SMF percentage from Paul’s spreadsheet) while the MMF percentage will be .8*(MMF percentage from Paul’s spreadsheet.).     As an example if one assumes the following:

 

MMF reach is dropped to 75m

there are equal numbers of server to switch links using fiber and switch to switch links  

the switch to switch links use a 2:1 ratio for the single versus double-link

 

Paul’s spreadsheet would predict that in his population  there is only a 16.4% single mode usage.    That would change the overall ratio to 33% SMF to 67% MMF.  

 

Adding an additional lower cost shorter distance SMF spec would however complicate the analysis.    The big question would be how much of the 20% additional SMF market would go to the lower cost shorter distance spec.  If a large percentage does then the volume of the LR4 would drop potentially increasing its cost substantially.

 

 

Mike Dudek 

QLogic Corporation

Senior Manager Signal Integrity

26650 Aliso Viejo Parkway

Aliso Viejo  CA 92656

949 389 6269 - office.

Mike.Dudek@xxxxxxxxxx

 

 

From: Kolesar, Paul [mailto:PKOLESAR@xxxxxxxxxxxxx]
Sent: Thursday, November 24, 2011 6:28 AM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

David,

Thanks for your efforts on this fundamentally important topic, going so far at to involve the governing authority of IEEE for guidance and reassurance of the current practices.  While I still believe that the current practice is overly restrictive, I also appreciate the line that may be crossed if discussions stray to far afield on the topic of price.  I intend to abide by the guidance you have given. 

 

All,

With regard to translation between cost and price, there are several forces at work.  I previously mentioned the gorilla in the room.  There is also the equally important factor of production rate, for increased volumes often translate into decreased costs.  The comparison of cost must be couched in terms of volume, for it can be imbalanced to compare input costs of different proposals if they are stated with expectation of differing volumes.  I urge all contributions on costs to also provide them in the context of their volume assumptions.  We must also realize that if volume context is given in terms like “at equivalent volumes of X”, where X is volume of a baseline technology that is well along its maturity curve, such volumes for 100G technologies may be many years into the future.  Therefore a large gap may exist between present costs and distant future cost potential.  We must also remember to consider the fact that historically the market demand for our optical solutions tends to fall along an 80/20 rule, with 80% of the port volumes going to multimode and 20% going to single-mode. See http://www.ieee802.org/3/hssg/public/nov06/barbieri_01_1106.pdf

 

So we must be weary of using the volumes of multimode solutions as the volume basis for cost projections of proposed single-mode solutions unless those single-mode solutions are presumed to replace multimode solutions and not just augment them in data centers.

 

The above contribution also provides historical adoption rates of single-mode solutions by reach that can set context for expectations.    

 

Regards,

Paul

 

-----Original Message-----
From: Law, David [mailto:dlaw@xxxxxx]
Sent: Thursday, November 24, 2011 1:52 AM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Hi Paul,

 

I want to bring your attention to the text 'Discussion of the cost of inputs necessary to create a compliant implementation of a standard are treated differently from discussions of prices at which compliant implementations can or should be sold. There is no useful or appropriate reason to discuss selling prices of implementations - each implementer of the standard should use its own independent business judgment to make that decision. In contrast, there is a legitimate reason to discuss costs of inputs used in implementation.'.

 

I believe this agrees with your point that the information is publically available - but states 'There is no useful or appropriate reason to discuss selling prices of implementations' which I believe is what you are requesting.

 

If a discussion of current and past end user cost (price) of products that implement the standard were to occur it could very easily stray into a discussion of the future end user costs of the proposed standard, which you agree is not allowed. This is addressed in the answer to the question 'So is it okay to talk about prices or output levels in an IEEE-SA meeting as long as we don’t reach an agreement?' which states:

 

No, it’s not okay. First, you can’t always control where the discussion will go – it may end up in undesired areas. Second, if agreeing on the subject would be unlawful (such as the respective selling prices of compliant products), then that subject should not be discussed. And third, it’s not up to you to decide whether your words and conduct amount to an agreement – in the U.S., that decision gets made by a judge using the peculiar rules of evidence that only courts use and by a jury that is unlikely to know anything about your industry or business. The whole question about your actions will come up after the fact, and with the sure vision of hindsight, any questionable discussion or debate could be seen to have led to a tacit if not an explicit agreement that is prohibited by law. Please do not put the IEEE, your company, your colleagues in the standards community, or yourself at risk by discussing these topics.

 

I have discussed your concerns with David Ringle, Director, Governance & Technical Committee Programs at the IEEE-SA, and he is in agreement with my position.

 

Best regards,

  David

_______________________________________

 

From: Kolesar, Paul [mailto:PKOLESAR@xxxxxxxxxxxxx]

Sent: 17 November 2011 17:22

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

David,

Thanks for the pointers to the IEEE policy.  I have been reviewing it and find the following particularly relevant to the thread below.  I have underlined key parts for easier reference. 

 

What else can we discuss? IEEE wants you to have the maximum flexibility to discuss topics relevant to developing a standard while also adhering to certain rules designed to minimize risk. It is impossible to identify all the topics that you can discuss, but here are some that you cannot discuss:

• prices at which products or services implementing the standard should be sold (“price” includes discounts, terms, and other conditions of sale);

• profits or profit margins;

• individual companies’ market shares or sales territories;

• allocation of customers, markets, production levels, or territories; or restricting the customers to whom, or territories in which, a company may sell or resell products;

• using standards or certification programs to exclude suppliers or competitors from the marketplace for any reason other than cost-performance or technical considerations;

• conditioning the implementation of a standard on the implementer’s use of products or services from a particular supplier [such as requiring use of a particular manufacturer’s components or requiring implementers to use a particular service provider(s) for compliance certification];

• bidding (or terms of bids) or refraining from bidding to sell any product or service;

• any matter which restricts any company’s independence in setting prices, establishing production and sales levels, choosing the markets in which it operates, or the manner in which it selects its customers and suppliers.

 

The first bullet gets at the heart of the matter.  It is what everyone keys on when the discussions of price are thwarted.  It states we cannot discuss what prices should be.  I think we can all agree that to do so would be anti-competitive.  But it says nothing about discussions of prices as they actually are in the market today or have been in the past.  To muzzle such discussions is overstepping the bounds and scope of the policy, for there is no anti-trust reason why prices that are in public domain, such as can be found posted on public web sites, cannot be brought forward.  Such activity is not price fixing, it is price reporting.

 

In the case of setting new standards we are naturally talking about documents that affect the future.  This is the context under which the IEEE policy is written and should be interpreted and applied.  When the policy says:

 

Discussion of the cost of inputs necessary to create a compliant implementation of a standard are treated differently from discussions of prices at which compliant implementations can or should be sold. There is no useful or appropriate reason to discuss selling prices of implementations – each implementer of the standard should use its own independent business judgment to make that decision. In contrast, there is a legitimate reason to discuss costs of inputs used in implementation.

 …

 

With regard to the costs of inputs used in implementing a standard, the only permitted discussion is the degree to which such costs may differ. Examples of permissible discussion topics would include differences in comparative component costs, operating costs, licensing costs, or the aggregate of such costs. The importance of this restriction on discussion is reinforced by the understanding that participants in the development of a standard often come from multiple stages of the supply chain (e.g., the input cost of a component to a system manufacturer is the output price of a component supplier).

 

Thus, in standards development technical activities, participants may discuss the relative costs (in terms, for example, of percentage increases or decreases) of different proposed technical approaches in comparison with the relative technical performance increases or decreases of those proposals.

 

It is obviously referring to the setting of new standards.  This is conveyed by the use of the word “proposed” and more fundamentally by the entire context of the policy for guiding standards development.  While it is not referring to discussions of cost for implementations already standardized and in the market, the above restrictions are needlessly being applied that way.  There is no anti-trust implication to discussions of publicly available information, even if it is with regard to price.  How can there be?  It’s already fully available to all participants. Such restrictions would imply that discussions of current prices somehow set agreements on future prices of yet-to-be-standardized implementations.  That is a non-sequitur. 

 

If we are talking about input costs on items affecting the setting of future standards, the guidelines are clear that we must use relative costs, not absolute costs.

 

It also recognizes the supply chain issue, that one link’s cost is the previous link’s price.  But it places no restriction on the point in the supply chain at which relative costs can be compared.  Therefore imposition of restrictions on discussions of relative costs at the top of the supply chain or any other specific part of the supply chain is outside of this policy.

 

While I do not relish raising these issues, I feel compelled to do so because after reading the actual policy it is clear to me that our practices in 802.3 are unnecessarily restrictive both to the letter and spirit of the IEEE policy.

 

Regards,

Paul

 

-----Original Message-----

From: Law, David [mailto:dlaw@xxxxxx]

Sent: Thursday, November 17, 2011 8:02 AM

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Hi Jonathan,

 

While I note that Dan has already stated that comparing cost at the end user is not permitted, and discussion did not go into that area, I wanted to reiterate that such discussion are not permitted. I also wanted to respond to your request to me to comment.

 

As I have often stated at meetings, I would encourage everybody to read the IEEE policy document 'Promoting Competition and Innovation: What You Need to Know about the IEEE Standards Association’s Antitrust and Competition Policy' <http://standards.ieee.org/develop/policies/antitrust.pdf>. I personally think it provides a good explanation of why these rules are in place, due to the Antitrust and competition laws throughout the world, and the consequences if they are not followed.

 

This policy states that we cannot discuss, among other items, 'prices at which products or services implementing the standard should be sold (“price” includes discounts, terms, and other conditions of sale)'. This is enforced in subclause 5.3.10.3 'Discussion of relative cost/benefit analyses' of the IEEE-SA Standards Board Operations Manual and stated in the 'Guidelines for IEEE-SA Meetings' slide shown at every meeting.

 

By way of an introduction to why these rules are in place, and the consequences to all of us if they are not followed, I offer the following extract from the introduction to the above policy document. Clause 2 of this document addresses 'Cost Discussions' in further detail. Participants may also wish to consult 'What You Need to Know About IEEE Standards and the Law' <http://standards.ieee.org/develop/policies/stdslaw.pdf>.

 

----

 

Promoting Competition and Innovation: What You Need to Know about the IEEE Standards Association’s Antitrust and Competition Policy

 

Antitrust and competition laws throughout the world rest on the premise that competition in the provision of products and services is the best way to ensure that consumers and other users receive maximum innovation and quality at the lowest possible prices. But sometimes effective competition requires a measure of cooperation among competing firms.

 

Standards development is one of those areas. Standards development serves one part of the IEEE’s mission – advancement of global prosperity by fostering technological innovation – but it can do so only if the standards development is conducted consistent with the antitrust and competition laws that regulate the nature and extent of cooperation in which competitors can legitimately engage.

 

The IEEE-SA is an international membership organization that provides a standards program serving the global needs of industry, government, and the public. A violation (or claims of violation) of competition laws will jeopardize what all participants are working so hard to build; will impede the IEEE mission; and may expose participants and their employers to the risk of imprisonment and other criminal penalties, civil remedies, and significant litigation costs. Even if a competition-law case or investigation is ultimately dropped, that will often happen only after the parties have spent considerable resources in responding to information requests and defending against the claims.

 

The IEEE-SA wants to help all of its participants avoid competition-law problems. Many IEEE-SA participants receive antitrust/competition-law compliance training from their employers, and IEEE-SA participants should always consult with their own or their company counsel when they have competition-law-related questions. This brochure is not intended to replace that competition-law training, advice, or other competition-law-related resources that participants may have available to them; rather, this brochure is intended to highlight the competition-law risks that are most pertinent to standards development and to explain the IEEE-SA’s policies with respect to competition law matters.

 

<http://standards.ieee.org/develop/policies/antitrust.pdf>

 

----

 

Best regards,

  David

 

________________________________________

From: Daniel Dove [mailto:ddove@xxxxxxx]

Sent: 16 November 2011 20:04

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Hi Robert,

 

I am not sure its even appropriate to comment about prices-of-resale. Its a topic better left understood without discussion within the IEEE. We all have a general idea of the challenges we face in assessing relative cost.

 

In my opinion, you do it by looking at fundamental architectural components and their specifications. You do it by looking at cost from a form/fit/function perspective and leave out things like market pricing, demand or volume. You choose *cost* comparisons with components that have equivalent markets/volumes and then your comparison can have merit without getting into the esoteric aspects of the market.

 

Dan

 

From: Robert Lingle <rlingle@xxxxxxxxxxxxx>

Reply-To: Robert Lingle <rlingle@xxxxxxxxxxxxx>

Date: Wed, 16 Nov 2011 22:52:26 +0000

To: 100G Group <STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx>

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Jonathon,

 

I agree with your former sentiment about it being against IEEE guidelines, so we must not do it. I am sure Paul agrees.

 

However I don’t agree with the latter sentiment. I think Paul is pointing out a real quandary in our task. I think we can point out cases where the adoption of components has been substantially impacted by the prices-of-resale, over a lengthy period of time. I am not sure how long we would have to wait for the long term?

 

It seems to be a genuine difficulty in carrying out the analysis we all want to see.

 

I don’t have a solution.

 

Warm regards,

Robert

 

From: Jonathan King [mailto:jonathan.king@xxxxxxxxxxx]

Sent: Wednesday, November 16, 2011 5:15 PM

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Hi Paul,

 I cannot support comparing  cost at the end user, because (in my opinion) that is quite clearly a price, and would be contrary to IEEE guidelines.

 I would like David Law to weigh in on this.

 

In an efficient market economy, the cost of manufacture (not the cost of distribution) of a product, or group of products, is the best indicator for long term cost to the end user.  I think that’s what we (802.3) want to get some indicator of when striving for  ‘low cost’ solutions.

Best wishes

Jonathan

 

 

From: Kolesar, Paul [mailto:PKOLESAR@xxxxxxxxxxxxx]

Sent: Tuesday, November 15, 2011 8:30 PM

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

I also like Jack’s perspective foundation.  And I have to agree that a common small port form factor would be valuable.  

 

Regarding the PMD cost comparisons, I also agree that picking a common cost basis could eliminate translation problems that come with use of different bases.  For PMD relative costs I am fine with choosing either 10GE SR or LR because I don’t quite appreciate Chris’ concerns over the danger in using LR as the basis.  But if there is a problem, it seems like it could be avoided by eliminating the bit/sec factor and instead using simple cost.  

 

However, there is still the issue of picking the point in the supply chain at which the baseline cost is chosen.  It could be at the level of the transceiver manufacturer, or up one level to the switch manufacturer, or off on another branch to distributors, or up one level again to the end user.  There can be substantial differences in these costs, which is what likely gives rise to the “order of magnitude” perception disparity that Chris mentioned.  While we are forbidden to talk about it, it is the 500 pound gorilla in the room.  In some cases it tips the scales lightly and in other cases it leans its full weight.  Yet this weight is what is creating a 100GE market acceptance barrier in data center deployments.  

 

While there is clear cost reduction potential in reducing the multimode lane count based just on the improvement in media cost, the benefit of defining a new single-mode solution may depend largely on the gorilla, for if we go to a parallel solution the media will only get more costly.  So for me the biggest cost question is whether defining a new single-mode solution moves the gorilla from leaning heavily to leaning lightly. 

 

While I’d like to agree to use cost at the transceiver maker level as the basis, it cannot address this big question.  If used it will likely result in highly distorted perceptions and projections because it ignores the order-of-magnitude problem.  The only point in the supply chain where transceiver costs and cabling costs come together is at the end user level.  This dilemma is hitting me squarely as I try to further my work on the “Kolesar_Kalculator”.   I continue to wonder what good this tool will do if the PMD cost and cable cost are in two different silos without a common basis to bring them together, for it is the combination of the two that defines the total channel cost that we must optimize.  I need to find a way to appease the gorilla.  If only Fay Wray were here…   

 

________________________________________

From: Chris Cole [mailto:chris.cole@xxxxxxxxxxx]

Sent: Tuesday, November 15, 2011 7:33 PM

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: Re: [802.3_100GNGOPTX] Emerging new reach space

 

Hello Jack,

 

Nice historical perspective on the new reach space.

 

Do I interpret your email as proposing to call the new 150m to 1000m standard 100GE-MR4? ☺

 

One of the problems in using today’s 100GE-LR4 cost as a comparison metric for new optics is that there is at least an order of magnitude variation in the perception of what that cost is. Given such a wide disparity in perception, 25% can either be impressive or inadequate.

 

What I had proposed as reference baselines for making comparisons is 10GE-SR (VCSEL based TX), 10GE-LR (DFB laser based TX) and 10GE-ER (EML based TX) bit/sec cost. This not only allows us to make objective relative comparisons but also to decide if the technology is suitable for wide spread adoption by using rules of thumb like 10x the  bandwidth (i.e. 100G) at 4x the cost (i.e. 40% of 10GE-nR cost) at similar high volumes.

 

Using these reference baselines, in order for the new reach space optics to be compelling, they must have a cost structure that is referenced to a fraction of 10GE-SR (VCSEL based) cost, NOT referenced to a fraction of 10GE-LR (DFB laser based) cost. Otherwise, the argument can be made that 100GE-LR4 will get to a fraction of 10GE-LR cost, at similar volumes, so why propose something new.

 

Chris

 

From: Jack Jewell [mailto:jack@xxxxxxxxxxxxxx]

Sent: Tuesday, November 15, 2011 3:06 PM

To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx

Subject: [802.3_100GNGOPTX] Emerging new reach space

 

Following last week's meetings, I think the following is relevant to frame our discussions of satisfying data center needs for low-cost low-power interconnections over reaches in the roughly 150-1000m range. This is a "30,000ft view,"without getting overly specific. 

Throughout GbE, 10GbE, 100GbE and into our discussions of 100GbE NextGenOptics, there have been 3 distinct spaces, with solutions optimized for each: Copper, MMF, and SMF. With increasing data rates, both copper and MMF specs focused on maintaining minimal cost, and their reach lengths decreased. E.g. MMF reach was up to 550m in GbE, then 300m in 10GbE (even shorter reach defined outside of IEEE), then 100-150m in 100GbE. MMF reach for 100GbE NextGenOptics will be even shorter unless electronics like EQ or FEC are included. Concurrently, MMF solutions have become attractive over copper at shorter and shorter distances. Both copper and MMF spaces have "literally" shrunk. In contrast, SMF solutions have maintained a 10km reach (not worrying about the initial 5km spec in GbE, or 40km solutions). To maintain the 10km reach, SMF solutions evolved from FP lasers, to DFB lasers, to WDM with cooled DFB lasers. The 10km solutions increasingly resemble longer-haul telecom solutions.!

  There is an increasing cost disparity between MMF and SMF solutions. This is an observation, not a questioning of the reasons behind these trends. The increasing cost disparity between MMF and SMF solutions is accompanied by rapidly-growing data center needs for links longer than MMF can accommodate, at costs less than 10km SMF can accommodate. This has the appearance of the emergence of a new "reach space," which warrants its own optimized solution. The emergence of the new reach space is the crux of this discussion.

Last week, a straw poll showed heavy support for "a PMD supporting a 500m reach at 25% the cost of 100GBASE-LR4" (heavily favored over targets of 75% or 50% the cost of 100GBASE-LR4). By heavily favoring the most aggressive low-cost target, this vote further supports the need for an "optimized solution" for this reach space. By "optimized solution" I mean one which is free from constraints, e.g. interoperability with other solutions. Though interoperability is desirable, an interoperable solution is unlikely to achieve the cost target. In the 3 reach spaces discussed so far, there is NO interoperability between copper/MMF, MMF/SMF, or copper/SMF. Copper, MMF and SMF are optimized solutions. It will likely take an optimized solution to satisfy this "mid-reach" space at the desired costs. To repeat: This has the appearance of the emergence of a new "reach space," which warrants its own optimized solution. Since the reach target lies between "short reach" and "long reach," "mi!

 d reach" is a reasonable term

Without discussing specific technical solutions, it is noteworthy that all 4 technical presentations last week for this "mid-reach" space involved parallel SMF, which would not interoperate with either 100GBASE-LR4, MMF, or copper. They would be optimized solutions, and interest in their further work received the highest support in straw polls. Given the high-density environment of datacenters, a solution for the mid-reach space would have most impact if its operating power was sufficiently low to be implemented in a form factor compatible with MMF and copper sockets.

Cheers, Jack