Ho Thong,
Reducing the probing voltage across the port down to 7.6V can fix the
consistency of the numbers however lower voltages will cause greater errors
for Rsignature measurements.
The two point measurements do not cancel totally the effect of the diodes
drop in the PD due to differences in the voltage drop as a function of the
current through the diode.
If I'll have the time I'll write and send you the analysis showing this
effect prior to next week meeting.
The only issue left to check is if we will get positive detection if two
PSE's are connected together and I am checking it.

So the picture as I see right now is:
1. Using large probing voltage range is OK (2.8 to 10V).
2. Using the upper voltage range is best from accuracy point of view.
3. Using the option of current source I agree that there is no problem
however the use of Voltage source
   should be free of problems too and all numbers should be consistent.
4. Using the 1st quadrant circuit is OK too, again the high impedance
circuit should be well defined too.
5. We need to check that positive detection will not occur under the
limitations and tolerances that we have
   defined and presented by Rick's work.

Regards

Yair





-----Original Message-----
From: Huynh, Thong [mailto:Thong_Huynh@xxxxxxxxxxx]
Sent: Wednesday, January 09, 2002 5:08 AM
To: 'Yair Darshan'; 'Jetzt, John J'
Cc: 'stds-802-3-pwrviamdi@xxxxxxxx'
Subject: RE: [802.3af] 45Kmin instead of 70Kmin ?


Hi Yair,

Ok, so if the input voltage is limited to 30V, the PD voltage will be at
30V(23.75k/(23.75k+70k)) = 7.6V.  The detection voltage range is  reduced by
2.4V, but this would not cause at any problem at all.  You still have the
2.8V to 7.6V range to work with.

If the PSE uses a current source to probe the PD, then there is no problem
to pump the PD voltage up to 10V if it so choose.

Impedance rule does not apply to PSE probe using  first quadrant voltage
source.

Conclusion:  changing the spec. from 70k to 45k is unnecessary and I would
oppose it.  But thanks to Yair for many of his good comments and
contributions so far.

===========================================
Thong Huynh
Senior Corporate Application Engineer, Standard Products Business Unit
Maxim Integrated Products
Tel:  408-530-6375
Fax:  408-222-1737
Email:  Thong_Huynh@xxxxxxxxxxx

> -----Original Message-----
> From:   Yair Darshan [SMTP:YairD@xxxxxxxxxxxxxx]
> Sent:   Tuesday, January 08, 2002 3:55 AM
> To:     'Jetzt, John J'
> Cc:     'stds-802-3-pwrviamdi@xxxxxxxx'
> Subject:     [802.3af] 45Kmin instead of 70Kmin ?
>
>
> Hi guys,
> We specified that the high impedance option for the detection circuit
> requires 70K min.
> We also specified that the voltage across the port is 2.8V to 10V.
> Now, if we want to get the 10V when we have the following conditions: 70K
> series resistance, Rsig=23.75K (25k - 5%)
> the probe source voltage need to be 10*(70k+23.75k)/23,75k=
> 10V*3.94=39.4V.
> We have limited the open circuit voltage to 30V max.
> So to get the 10V max we need to reduce the 70k min value to (30V*23.75K -
> 10V*23.75K)/10V = 47.5K.
> Having 5% margin we get: 45K min.
> In case of PSE to PSE connection the worst case power dissipation over
> this
> resistor would be: 57^2/45k=72mW which is <125mW.
>
> Thus to keep all numbers consistent with the intentions I suggest to
> change
> from 70K min to 45K min.
>
> Do you see problems with this change?
>
> Thanks
>
> Yair.
>
>
> Darshan Yair
> Chief  Engineer
> > PowerDsine Ltd.  -  Powering Converged Networks
> > 1 Hanagar St., P.O. Box 7220
> > Neve Ne'eman Industrial Zone
> > Hod Hasharon 45421, Israel
> Tel:  +972-9-775-5100, Cell: +972-54-893019
> Fax: +972-9-775-5111
> > E-mail: <mailto:yaird@xxxxxxxxxxxxxx>.
> > http://www.powerdsine.com
> >
----------------------------------------------------------------------
Maxim Home Page:
http://www.maxim-ic.com
Products Page:
http://www.maxim-ic.com/MaximProducts/products.htm
New Products:
http://dbserv.maxim-ic.com/new_products.cfm
Datasheets:
http://dbserv.maxim-ic.com/l_datasheet3.cfm
-----------------------------------------------------------------------
The information contained in this message is confidential
and may be legally privileged. The message is intended
solely for the addressee(s). If you are not the intended
recipient,  you are hereby notified that any use, dissemination,
or reproduction is strictly prohibited and may be unlawful.
If you are not the intended recipient, please contact the sender
by return e-mail and destroy all copies of the original message.
--------------------------------------------------------------------------








----- End Included Message -----